bobkatz wrote on Wed, 15 December 2004 16:26 |
gtphill wrote on Wed, 15 December 2004 14:43 |
The second point is that I would use GFCI breakers on the secondary side of the isolation transformer. You are relying on your new ground rod (bonded to the center tap) to act as a current sink in case of a short.
|
Why? I'm bonding the neutral to the ground inside the new sub box, so similar to as you described to me on the phone, the neutral is the one that carries the return current for the hot phase, and really ensures we'll blow a breaker, and the ground is really a safety. Anyway, no harm in using GFCI breakers as long as I can keep my clean ground clean and isolated from the dirty ground of the box.
|
If the neutral should come unbonded to your ground, a standard breaker trips only if the resisitivity of the ground rod is low enough to sink the trip current of the breaker.
If however there is only a single ground, and that ground is bonded to the non-isolated neutral at the main panel, then then you are relying on the low resistivity of the power company's neutral to provide a sufficient current path to trip the (standard) breaker should something come unbonded. The power company's neutral returns to either a pole transformer or load station, and should have a lower resistivity that your local rod.
We won't even touch the issue of voltage differences between the power company ground and the service entrance ground...
The caveat to ultraquiet power with the single ground point method is you are now relying on the integrtity of the zero potential reference at the primary building ground (+ your 100ft of wiring) to sink neutral "trash" currents. Great if the neutral is a superconductor, but somewhat less than great with real wire. NEC is about safety, not ultra-clean audio.
Your proposed second ground rod configuration truly separates the neutral (ignoring any galvanic coupling in the soil), but then needs a GFCI-type breaker to insure the resistivity of the soil doesn't prevent enough current flow to trip a standard breaker
in the case of the neutral becoming unbonded.Quote: |
But I'm breaking this rule because the sub panel will contain an iso transformer, and therefore I can bond my NEW floating neutral to the ground that I also create within this new box, eh????
|
Yup. This is exactly what the power company is doing outside your house, with the added assurance of a low resistivity ground plane that they test in some manner. If you could insure the resistivity of the new ground, you'd have no issues with standard breakers. GFCI is just covering your butt.
For an object lesson, go ahead and short your hot and
ground on the secondary side of the transformer, with a breaker of course, both with and without the neutral bonded. Standard breaker should trip in the bonded case, and
might trip in the unbonded case. If it does trip in the unbonded case, you have a good low resistivity ground. Just don't pee on the ground rod during this process
This whole process of a separate "service" panel and new ground rod is legal under the NEC if the panel is located on a
separate structure (e.g. guest house), even though it's technically a subpanel of the main house. I'll dig up the section that's in.
Quote: |
Comments greatly desired. I'm putting it into my own FAQ for my own use as well. Thanks, Phil.
|
No problem. I'm not really breaking new ground here, just apeing my teachers. Once you grasp the take home message of my original post, and realize you can set up an e-field potential without a current having to flow, you've got 90% of it.